Re: EHU cable 1.5mm/2.5mm orange or blue?

Richard
 

But it does not say as you suggest and the wording does not avoid
electrically dangerous contraptions, so In my mind it is pointless!
Richard

On 16/02/2020 13:16, Bennett Family wrote:
They are trying to be safe - both for your benefit and others using the site.

Should probably say “not exceeding 25m” and whatever the wording needed to avoid home made, electrically dangerous contraptions!

Nobody has ever questioned my set up so I’m not too worried as the wording can be used to stop dangerous set ups.

Both Clubs have sites with consistently high standards. You know what you’re getting.

Martin

On 16 Feb 2020, at 13:07, Richard via Groups.Io <edelec=gmx.com@groups.io> wrote:

Thanks for the info.
Justifies my lack of membership. I really would love to know the
reasoning why a mains lead should be 25 +/- 2 metres long and how it is
determined that any particular lead is "Supplied by the van
manufacturer". Could one of you as a member actually ask the question in
the club magazine?
Richard



On 15/02/2020 17:24, Edelec wrote:
I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard
On 15/02/2020 16:53, Carol Weaver wrote:
Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.
Carol
On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:
Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly
available on the market are orange 2.5mm. These meet the standards
of the NCC and the CCC.
Also available but not so common are orange 1.5mm but these are
not approved by the NCC.
I’ve hated using the two 2.5mm orange cables that I’ve owned
because they have quickly become inflexible, tangled and hard to
wind up.
So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
says on the pack that it’s not suitable for caravan sites and
should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.
Go Outdoors Price is £30 but I found it for £22 on another website
and with their price guarantee, they sold it to me for £20. Bargain!
I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian
On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
<mailto:timsinc@...>> wrote:
On 15/02/2020, Andy Clarke <andyclarke1050@...
<mailto:andyclarke1050@...>> wrote:
25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
... and a heck of a lot easier to man/woman-handle. Except for CMC
sites, two even shorter cables connecting if needed (but rarely)
definitely my preferred option.
Campervan Tim
in storm-free, sunny Spain
UKMotorhomes.net
On Sat, 15 Feb 2020 at 12:33, Bennett Family
<martin@... <mailto:martin@...>>
wrote:
Andy, Ern
Thanks.
Any idea of the weight difference for a 25m length of each? I
doubt f it
will be significant in the grand scheme of things.
Martin
On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
<andyclarke1050=
gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:

1.5mm cable is OK for up to 3kW assuming an allowable voltage
drop of 5%
and that the cable is in free air, i.e. not on a reel or
closely coiled.
Andy Clarke
www.ukmotorhomes.net <http://www.ukmotorhomes.net>
On Fri, 14 Feb 2020 at 21:05, Bennett Family
<martin@... <mailto:martin@...>>
wrote:
Is there any advantage in using 2.5mm rather than 1.5mm given
that most
of us are unlikely to use more than 2kw?
Just demonstrating my ignorance.
If no advantage then the lighter weight, blue, cable would
seem to make
sense.
Martin
--
*It'll all be OK in the end. If it's not OK, it's not the end*
--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please

Re: EHU cable 1.5mm/2.5mm orange or blue?

Bennett Family
 

They are trying to be safe - both for your benefit and others using the site.

Should probably say “not exceeding 25m” and whatever the wording needed to avoid home made, electrically dangerous contraptions!

Nobody has ever questioned my set up so I’m not too worried as the wording can be used to stop dangerous set ups.

Both Clubs have sites with consistently high standards. You know what you’re getting.

Martin

On 16 Feb 2020, at 13:07, Richard via Groups.Io <edelec=gmx.com@groups.io> wrote:

Thanks for the info.
Justifies my lack of membership. I really would love to know the
reasoning why a mains lead should be 25 +/- 2 metres long and how it is
determined that any particular lead is "Supplied by the van
manufacturer". Could one of you as a member actually ask the question in
the club magazine?
Richard



On 15/02/2020 17:24, Edelec wrote:
I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard
On 15/02/2020 16:53, Carol Weaver wrote:
Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.
Carol
On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:
Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly
available on the market are orange 2.5mm. These meet the standards
of the NCC and the CCC.
Also available but not so common are orange 1.5mm but these are
not approved by the NCC.
I’ve hated using the two 2.5mm orange cables that I’ve owned
because they have quickly become inflexible, tangled and hard to
wind up.
So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
says on the pack that it’s not suitable for caravan sites and
should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.
Go Outdoors Price is £30 but I found it for £22 on another website
and with their price guarantee, they sold it to me for £20. Bargain!
I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian
On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
<mailto:timsinc@...>> wrote:
On 15/02/2020, Andy Clarke <andyclarke1050@...
<mailto:andyclarke1050@...>> wrote:
25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
... and a heck of a lot easier to man/woman-handle. Except for CMC
sites, two even shorter cables connecting if needed (but rarely)
definitely my preferred option.
Campervan Tim
in storm-free, sunny Spain
UKMotorhomes.net
On Sat, 15 Feb 2020 at 12:33, Bennett Family
<martin@... <mailto:martin@...>>
wrote:
Andy, Ern
Thanks.
Any idea of the weight difference for a 25m length of each? I
doubt f it
will be significant in the grand scheme of things.
Martin
On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
<andyclarke1050=
gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:

1.5mm cable is OK for up to 3kW assuming an allowable voltage
drop of 5%
and that the cable is in free air, i.e. not on a reel or
closely coiled.
Andy Clarke
www.ukmotorhomes.net <http://www.ukmotorhomes.net>
On Fri, 14 Feb 2020 at 21:05, Bennett Family
<martin@... <mailto:martin@...>>
wrote:
Is there any advantage in using 2.5mm rather than 1.5mm given
that most
of us are unlikely to use more than 2kw?
Just demonstrating my ignorance.
If no advantage then the lighter weight, blue, cable would
seem to make
sense.
Martin
--
*It'll all be OK in the end. If it's not OK, it's not the end*
--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please

Re: EHU cable 1.5mm/2.5mm orange or blue?

Richard
 

Thanks for the info.
Justifies my lack of membership. I really would love to know the
reasoning why a mains lead should be 25 +/- 2 metres long and how it is
determined that any particular lead is "Supplied by the van
manufacturer". Could one of you as a member actually ask the question in
the club magazine?
Richard

On 15/02/2020 17:24, Edelec wrote:
I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard

On 15/02/2020 16:53, Carol Weaver wrote:

Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.

Carol

On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:

    Thanks to all for your thoughts.
    My further research indicates that standard ehu cables commonly
    available on the market are orange 2.5mm. These meet the standards
    of the NCC and the CCC.

    Also available but not so common are orange 1.5mm but these are
    not approved by the NCC.

    I’ve hated using the two 2.5mm orange cables that I’ve owned
    because they have quickly become inflexible, tangled  and hard to
    wind up.

    So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
    says on the pack that it’s not suitable for caravan sites and
    should not be used in wet or damp conditions!!
    However, it is marketed as a Motorhome ehu on many websites.
    So that’s a bit mysterious.

    Go Outdoors Price is £30 but I found it for £22 on another website
    and with their price guarantee, they sold it to me for £20. Bargain!

    I’m sure it will be fine.
    And my heart won’t sink when I need to use a hook up.
    Cheers
    Brian



    > On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
    <mailto:timsinc@...>> wrote:
    >
    > On 15/02/2020, Andy Clarke <andyclarke1050@...
    <mailto:andyclarke1050@...>> wrote:
    >> 25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
    >>
    >
    > ... and a heck of a lot easier to man/woman-handle. Except for CMC
    > sites, two even shorter cables connecting if needed (but rarely)
    > definitely my preferred option.
    >
    > Campervan Tim
    > in storm-free, sunny Spain
    >
    >
    >
    >> UKMotorhomes.net
    >>
    >>> On Sat, 15 Feb 2020 at 12:33, Bennett Family
    <martin@... <mailto:martin@...>>
    >>> wrote:
    >>>
    >>> Andy, Ern
    >>>
    >>> Thanks.
    >>>
    >>> Any idea of the weight difference for a 25m length of each? I
    doubt f it
    >>> will be significant in the grand scheme of things.
    >>>
    >>> Martin
    >>>
    >>>
    >>> On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
    <andyclarke1050=
    >>> gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:
    >>>
    >>> 
    >>> 1.5mm cable is OK for up to 3kW assuming an allowable voltage
    drop of 5%
    >>> and that the cable is in free air, i.e. not on a reel or
    closely coiled.
    >>>
    >>> Andy Clarke
    >>> www.ukmotorhomes.net <http://www.ukmotorhomes.net>
    >>>
    >>> On Fri, 14 Feb 2020 at 21:05, Bennett Family
    <martin@... <mailto:martin@...>>
    >>> wrote:
    >>>
    >>>> Is there any advantage in using 2.5mm rather than 1.5mm given
    that most
    >>>> of us are unlikely to use more than 2kw?
    >>>> Just demonstrating my ignorance.
    >>>> If no advantage then the lighter weight, blue, cable would
    seem to make
    >>>> sense.
    >>>>
    >>>> Martin
    >>>>
    >>>>
    >>>
    >>>
    >>
    >>
    >>
    >>
    >
    >
    > --
    >
    > *It'll all be OK in the end. If it's not OK, it's not the end*
    >
    >
    >



--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please

Re: Jobsworth

Peter S
 

At the CC Hawes site we were given a cable by the warden to connect to a bollard that was too far away to reach with one cable. The bollard nearest to the van was out of order.

 

Peter S

 

From: motorhome-list@groups.io [mailto:motorhome-list@groups.io] On Behalf Of Bennett Family
Sent: 16 February 2020 10:46
To: motorhome-list@groups.io
Subject: Re: [motorhome-list] Jobsworth

 

Carol,

 

Both clubs have pluses & minuses. Both have improved significantly over the years - particularly in the way they have moved towards accepting motorhomes and the CMC in being less regimented. 

 

We join both and think them worth the annual fee. 

 

Martin



On 16 Feb 2020, at 10:37, Carol Weaver via Groups.Io <corconx@...> wrote:



 

We found overtime that the cc club was worse for rules and the ccc

When it came time to decide on one we chose the ccc as we late their THS and more relaxed rules

 

C

 

On Sun, 16 Feb 2020 at 10:18, Bennett Family <martin@...> wrote:


We turned up at the the CMC St David’s site on the day the Fastnet Race had been cancelled because of the gale and parts of Wales had been declared a disaster area.

Unsurprisingly, the site wasn’t crowded! We parked facing into the wind to avoid the battering and the Warden asked us to move as we were not in line with their marker post!

I refused and he said that if the fire brigade came to check I’d be in trouble. I did  point out that
A. It’s a disaster area and surely the fire service had better things to do and
B. There was nobody else daft enough to be on the site!

Martin

> On 16 Feb 2020, at 09:27, timsinc Sinclair via Groups.Io <timsinc=gmail.com@groups.io> wrote:
>
> Thank you, Mr Jobsworth, for making camping such empowering, relaxed
> fun......Definitely hooked up on it !!!.
>
> Talking to a former CMC warden holidaying at this near Granada
> campsite, relating some of the rules, such as tools (like even small
> pair of plyers) on site had all to be of certain approved standard. As
> did the box.
>
> One day, a motorhomer asked him if he could borrow step ladder to sort
> out a problem with high-up awning. "Sorry, we're not allowed to lend
> any equipment". If he fell off, the club might be sued.
>
> But what my ex-warden then said to the man: "I'm off to clean the loos
> and the step ladder happens to be beside that gate over there."
>
> Thankfully, they're not all Jobsworths. To be certain to avoid one,
> give Henley-on-Thames CMC site a miss, although does depend on who is
> on duty.
>
> Campervan Tim
>
>> On 16/02/2020, Bennett Family <martin@...> wrote:
>> CMC rules seem to make cables of less than 23m “illegal” even if next to the
>> bollard - so best dump your short cable and ensure that your full sized
>> replacement has been supplied by the “caravan manufacturer” - would be as
>> well to have a receipt. Disconnect in very cold weather as it may not pass
>> the “flexible” test.
>>
>> Jobsworth
>> On 16 Feb 2020, at 08:25, timsinc Sinclair via Groups.Io
>> <timsinc=gmail.com@groups.io> wrote:
>>
>> 
>> Well, the CMC rules say: "The maximum permitted distance between socket
>> outlet and any point on the caravan pitch is 20 metres.
>> "The hook up lead should be 25 metres (+/- 2 metres) of flexible cable
>> supplied by the caravan manufacturer."
>> That's where and why, I suppose, joing together of two cables frowned upon.
>> The CCC have a much more relaxed attitude.
>>
>> No mention of colour or size. Usual stuff about completely unwinding and not
>> leaving plugged into bollard if off for the day - or even doing the
>> empty/filling biz.
>>
>> "Club site staff have authority to refuse to offer a power supply to a
>> caravan if it is believed that the installation may be unsafe."
>>
>> Yep, often down to how officious a warden is.
>>
>> Campervan Tim
>>
>>
>>
>>
>> On 15 February 2020 5:26:56 pm "Adrian Harman" <adrianharman@...>
>> wrote:
>>
>> I’m also confused??
>>
>> Adrian
>> On 15 Feb 2020, 17:24 +0000, Richard <edelec@...>, wrote:
>> I am amazed at what I am reading! What are these caravan rules with
>> regard to cables?
>> Richard
>>
>> On 15/02/2020 16:53, Carol Weaver wrote:
>>
>> Well our blue one has been used on both CCC and old CC (not in latter
>> now) without any problems.
>>
>> Carol
>>
>> On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
>> <mailto:brianinspain12@...>> wrote:
>>
>> Thanks to all for your thoughts.
>> My further research indicates that standard ehu cables commonly
>> available on the market are orange 2.5mm. These meet the standards
>> of the NCC and the CCC.
>>
>> Also available but not so common are orange 1.5mm but these are
>> not approved by the NCC.
>>
>> I’ve hated using the two 2.5mm orange cables that I’ve owned
>> because they have quickly become inflexible, tangled  and hard to
>> wind up.
>>
>> So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
>> says on the pack that it’s not suitable for caravan sites and
>> should not be used in wet or damp conditions!!
>> However, it is marketed as a Motorhome ehu on many websites.
>> So that’s a bit mysterious.
>>
>> Go Outdoors Price is £30 but I found it for £22 on another website
>> and with their price guarantee, they sold it to me for £20. Bargain!
>>
>> I’m sure it will be fine.
>> And my heart won’t sink when I need to use a hook up.
>> Cheers
>> Brian
>>
>>
>>
>> On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
>> <mailto:timsinc@...>> wrote:
>>
>> On 15/02/2020, Andy Clarke <andyclarke1050@...
>> <mailto:andyclarke1050@...>> wrote:
>> 25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
>>
>>
>> ... and a heck of a lot easier to man/woman-handle. Except for CMC
>> sites, two even shorter cables connecting if needed (but rarely)
>> definitely my preferred option.
>>
>> Campervan Tim
>> in storm-free, sunny Spain
>>
>>
>>
>> UKMotorhomes.net
>>
>> On Sat, 15 Feb 2020 at 12:33, Bennett Family
>> <martin@... <mailto:martin@...>>
>> wrote:
>>
>> Andy, Ern
>>
>> Thanks.
>>
>> Any idea of the weight difference for a 25m length of each? I
>> doubt f it
>> will be significant in the grand scheme of things.
>>
>> Martin
>>
>>
>> On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
>> <andyclarke1050=
>> gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:
>>
>> 
>> 1.5mm cable is OK for up to 3kW assuming an allowable voltage
>> drop of 5%
>> and that the cable is in free air, i.e. not on a reel or
>> closely coiled.
>>
>> Andy Clarke
>> www.ukmotorhomes.net <http://www.ukmotorhomes.net>
>>
>> On Fri, 14 Feb 2020 at 21:05, Bennett Family
>> <martin@... <mailto:martin@...>>
>> wrote:
>>
>> Is there any advantage in using 2.5mm rather than 1.5mm given
>> that most
>> of us are unlikely to use more than 2kw?
>> Just demonstrating my ignorance.
>> If no advantage then the lighter weight, blue, cable would
>> seem to make
>> sense.
>>
>> Martin
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> --
>>
>> *It'll all be OK in the end. If it's not OK, it's not the end*
>>
>>
>>
>>
>>
>>
>> --
>> --
>> Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
>> <http://www.carolweaver.co.uk/Travel>
>> Plusnet -cardun if you sign up recommend me please
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>
>
> --
>
> *It'll all be OK in the end. If it's not OK, it's not the end*
>
>
>


--

--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
Plusnet -cardun if you sign up recommend me please

Re: Jobsworth

Bennett Family
 

Carol,

Both clubs have pluses & minuses. Both have improved significantly over the years - particularly in the way they have moved towards accepting motorhomes and the CMC in being less regimented. 

We join both and think them worth the annual fee. 

Martin


On 16 Feb 2020, at 10:37, Carol Weaver via Groups.Io <corconx@...> wrote:



We found overtime that the cc club was worse for rules and the ccc
When it came time to decide on one we chose the ccc as we late their THS and more relaxed rules

C

On Sun, 16 Feb 2020 at 10:18, Bennett Family <martin@...> wrote:

We turned up at the the CMC St David’s site on the day the Fastnet Race had been cancelled because of the gale and parts of Wales had been declared a disaster area.

Unsurprisingly, the site wasn’t crowded! We parked facing into the wind to avoid the battering and the Warden asked us to move as we were not in line with their marker post!

I refused and he said that if the fire brigade came to check I’d be in trouble. I did  point out that
A. It’s a disaster area and surely the fire service had better things to do and
B. There was nobody else daft enough to be on the site!

Martin

> On 16 Feb 2020, at 09:27, timsinc Sinclair via Groups.Io <timsinc=gmail.com@groups.io> wrote:
>
> Thank you, Mr Jobsworth, for making camping such empowering, relaxed
> fun......Definitely hooked up on it !!!.
>
> Talking to a former CMC warden holidaying at this near Granada
> campsite, relating some of the rules, such as tools (like even small
> pair of plyers) on site had all to be of certain approved standard. As
> did the box.
>
> One day, a motorhomer asked him if he could borrow step ladder to sort
> out a problem with high-up awning. "Sorry, we're not allowed to lend
> any equipment". If he fell off, the club might be sued.
>
> But what my ex-warden then said to the man: "I'm off to clean the loos
> and the step ladder happens to be beside that gate over there."
>
> Thankfully, they're not all Jobsworths. To be certain to avoid one,
> give Henley-on-Thames CMC site a miss, although does depend on who is
> on duty.
>
> Campervan Tim
>
>> On 16/02/2020, Bennett Family <martin@...> wrote:
>> CMC rules seem to make cables of less than 23m “illegal” even if next to the
>> bollard - so best dump your short cable and ensure that your full sized
>> replacement has been supplied by the “caravan manufacturer” - would be as
>> well to have a receipt. Disconnect in very cold weather as it may not pass
>> the “flexible” test.
>>
>> Jobsworth
>> On 16 Feb 2020, at 08:25, timsinc Sinclair via Groups.Io
>> <timsinc=gmail.com@groups.io> wrote:
>>
>> 
>> Well, the CMC rules say: "The maximum permitted distance between socket
>> outlet and any point on the caravan pitch is 20 metres.
>> "The hook up lead should be 25 metres (+/- 2 metres) of flexible cable
>> supplied by the caravan manufacturer."
>> That's where and why, I suppose, joing together of two cables frowned upon.
>> The CCC have a much more relaxed attitude.
>>
>> No mention of colour or size. Usual stuff about completely unwinding and not
>> leaving plugged into bollard if off for the day - or even doing the
>> empty/filling biz.
>>
>> "Club site staff have authority to refuse to offer a power supply to a
>> caravan if it is believed that the installation may be unsafe."
>>
>> Yep, often down to how officious a warden is.
>>
>> Campervan Tim
>>
>>
>>
>>
>> On 15 February 2020 5:26:56 pm "Adrian Harman" <adrianharman@...>
>> wrote:
>>
>> I’m also confused??
>>
>> Adrian
>> On 15 Feb 2020, 17:24 +0000, Richard <edelec@...>, wrote:
>> I am amazed at what I am reading! What are these caravan rules with
>> regard to cables?
>> Richard
>>
>> On 15/02/2020 16:53, Carol Weaver wrote:
>>
>> Well our blue one has been used on both CCC and old CC (not in latter
>> now) without any problems.
>>
>> Carol
>>
>> On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
>> <mailto:brianinspain12@...>> wrote:
>>
>> Thanks to all for your thoughts.
>> My further research indicates that standard ehu cables commonly
>> available on the market are orange 2.5mm. These meet the standards
>> of the NCC and the CCC.
>>
>> Also available but not so common are orange 1.5mm but these are
>> not approved by the NCC.
>>
>> I’ve hated using the two 2.5mm orange cables that I’ve owned
>> because they have quickly become inflexible, tangled  and hard to
>> wind up.
>>
>> So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
>> says on the pack that it’s not suitable for caravan sites and
>> should not be used in wet or damp conditions!!
>> However, it is marketed as a Motorhome ehu on many websites.
>> So that’s a bit mysterious.
>>
>> Go Outdoors Price is £30 but I found it for £22 on another website
>> and with their price guarantee, they sold it to me for £20. Bargain!
>>
>> I’m sure it will be fine.
>> And my heart won’t sink when I need to use a hook up.
>> Cheers
>> Brian
>>
>>
>>
>> On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
>> <mailto:timsinc@...>> wrote:
>>
>> On 15/02/2020, Andy Clarke <andyclarke1050@...
>> <mailto:andyclarke1050@...>> wrote:
>> 25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
>>
>>
>> ... and a heck of a lot easier to man/woman-handle. Except for CMC
>> sites, two even shorter cables connecting if needed (but rarely)
>> definitely my preferred option.
>>
>> Campervan Tim
>> in storm-free, sunny Spain
>>
>>
>>
>> UKMotorhomes.net
>>
>> On Sat, 15 Feb 2020 at 12:33, Bennett Family
>> <martin@... <mailto:martin@...>>
>> wrote:
>>
>> Andy, Ern
>>
>> Thanks.
>>
>> Any idea of the weight difference for a 25m length of each? I
>> doubt f it
>> will be significant in the grand scheme of things.
>>
>> Martin
>>
>>
>> On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
>> <andyclarke1050=
>> gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:
>>
>> 
>> 1.5mm cable is OK for up to 3kW assuming an allowable voltage
>> drop of 5%
>> and that the cable is in free air, i.e. not on a reel or
>> closely coiled.
>>
>> Andy Clarke
>> www.ukmotorhomes.net <http://www.ukmotorhomes.net>
>>
>> On Fri, 14 Feb 2020 at 21:05, Bennett Family
>> <martin@... <mailto:martin@...>>
>> wrote:
>>
>> Is there any advantage in using 2.5mm rather than 1.5mm given
>> that most
>> of us are unlikely to use more than 2kw?
>> Just demonstrating my ignorance.
>> If no advantage then the lighter weight, blue, cable would
>> seem to make
>> sense.
>>
>> Martin
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> --
>>
>> *It'll all be OK in the end. If it's not OK, it's not the end*
>>
>>
>>
>>
>>
>>
>> --
>> --
>> Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
>> <http://www.carolweaver.co.uk/Travel>
>> Plusnet -cardun if you sign up recommend me please
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>
>
> --
>
> *It'll all be OK in the end. If it's not OK, it's not the end*
>
>
>



--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
Plusnet -cardun if you sign up recommend me please

Re: Jobsworth

Carol Weaver
 


We found overtime that the cc club was worse for rules and the ccc
When it came time to decide on one we chose the ccc as we late their THS and more relaxed rules

C


On Sun, 16 Feb 2020 at 10:18, Bennett Family <martin@...> wrote:

We turned up at the the CMC St David’s site on the day the Fastnet Race had been cancelled because of the gale and parts of Wales had been declared a disaster area.

Unsurprisingly, the site wasn’t crowded! We parked facing into the wind to avoid the battering and the Warden asked us to move as we were not in line with their marker post!

I refused and he said that if the fire brigade came to check I’d be in trouble. I did  point out that
A. It’s a disaster area and surely the fire service had better things to do and
B. There was nobody else daft enough to be on the site!

Martin

> On 16 Feb 2020, at 09:27, timsinc Sinclair via Groups.Io <timsinc=gmail.com@groups.io> wrote:
>
> Thank you, Mr Jobsworth, for making camping such empowering, relaxed
> fun......Definitely hooked up on it !!!.
>
> Talking to a former CMC warden holidaying at this near Granada
> campsite, relating some of the rules, such as tools (like even small
> pair of plyers) on site had all to be of certain approved standard. As
> did the box.
>
> One day, a motorhomer asked him if he could borrow step ladder to sort
> out a problem with high-up awning. "Sorry, we're not allowed to lend
> any equipment". If he fell off, the club might be sued.
>
> But what my ex-warden then said to the man: "I'm off to clean the loos
> and the step ladder happens to be beside that gate over there."
>
> Thankfully, they're not all Jobsworths. To be certain to avoid one,
> give Henley-on-Thames CMC site a miss, although does depend on who is
> on duty.
>
> Campervan Tim
>
>> On 16/02/2020, Bennett Family <martin@...> wrote:
>> CMC rules seem to make cables of less than 23m “illegal” even if next to the
>> bollard - so best dump your short cable and ensure that your full sized
>> replacement has been supplied by the “caravan manufacturer” - would be as
>> well to have a receipt. Disconnect in very cold weather as it may not pass
>> the “flexible” test.
>>
>> Jobsworth
>> On 16 Feb 2020, at 08:25, timsinc Sinclair via Groups.Io
>> <timsinc=gmail.com@groups.io> wrote:
>>
>> 
>> Well, the CMC rules say: "The maximum permitted distance between socket
>> outlet and any point on the caravan pitch is 20 metres.
>> "The hook up lead should be 25 metres (+/- 2 metres) of flexible cable
>> supplied by the caravan manufacturer."
>> That's where and why, I suppose, joing together of two cables frowned upon.
>> The CCC have a much more relaxed attitude.
>>
>> No mention of colour or size. Usual stuff about completely unwinding and not
>> leaving plugged into bollard if off for the day - or even doing the
>> empty/filling biz.
>>
>> "Club site staff have authority to refuse to offer a power supply to a
>> caravan if it is believed that the installation may be unsafe."
>>
>> Yep, often down to how officious a warden is.
>>
>> Campervan Tim
>>
>>
>>
>>
>> On 15 February 2020 5:26:56 pm "Adrian Harman" <adrianharman@...>
>> wrote:
>>
>> I’m also confused??
>>
>> Adrian
>> On 15 Feb 2020, 17:24 +0000, Richard <edelec@...>, wrote:
>> I am amazed at what I am reading! What are these caravan rules with
>> regard to cables?
>> Richard
>>
>> On 15/02/2020 16:53, Carol Weaver wrote:
>>
>> Well our blue one has been used on both CCC and old CC (not in latter
>> now) without any problems.
>>
>> Carol
>>
>> On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
>> <mailto:brianinspain12@...>> wrote:
>>
>> Thanks to all for your thoughts.
>> My further research indicates that standard ehu cables commonly
>> available on the market are orange 2.5mm. These meet the standards
>> of the NCC and the CCC.
>>
>> Also available but not so common are orange 1.5mm but these are
>> not approved by the NCC.
>>
>> I’ve hated using the two 2.5mm orange cables that I’ve owned
>> because they have quickly become inflexible, tangled  and hard to
>> wind up.
>>
>> So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
>> says on the pack that it’s not suitable for caravan sites and
>> should not be used in wet or damp conditions!!
>> However, it is marketed as a Motorhome ehu on many websites.
>> So that’s a bit mysterious.
>>
>> Go Outdoors Price is £30 but I found it for £22 on another website
>> and with their price guarantee, they sold it to me for £20. Bargain!
>>
>> I’m sure it will be fine.
>> And my heart won’t sink when I need to use a hook up.
>> Cheers
>> Brian
>>
>>
>>
>> On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
>> <mailto:timsinc@...>> wrote:
>>
>> On 15/02/2020, Andy Clarke <andyclarke1050@...
>> <mailto:andyclarke1050@...>> wrote:
>> 25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
>>
>>
>> ... and a heck of a lot easier to man/woman-handle. Except for CMC
>> sites, two even shorter cables connecting if needed (but rarely)
>> definitely my preferred option.
>>
>> Campervan Tim
>> in storm-free, sunny Spain
>>
>>
>>
>> UKMotorhomes.net
>>
>> On Sat, 15 Feb 2020 at 12:33, Bennett Family
>> <martin@... <mailto:martin@...>>
>> wrote:
>>
>> Andy, Ern
>>
>> Thanks.
>>
>> Any idea of the weight difference for a 25m length of each? I
>> doubt f it
>> will be significant in the grand scheme of things.
>>
>> Martin
>>
>>
>> On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
>> <andyclarke1050=
>> gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:
>>
>> 
>> 1.5mm cable is OK for up to 3kW assuming an allowable voltage
>> drop of 5%
>> and that the cable is in free air, i.e. not on a reel or
>> closely coiled.
>>
>> Andy Clarke
>> www.ukmotorhomes.net <http://www.ukmotorhomes.net>
>>
>> On Fri, 14 Feb 2020 at 21:05, Bennett Family
>> <martin@... <mailto:martin@...>>
>> wrote:
>>
>> Is there any advantage in using 2.5mm rather than 1.5mm given
>> that most
>> of us are unlikely to use more than 2kw?
>> Just demonstrating my ignorance.
>> If no advantage then the lighter weight, blue, cable would
>> seem to make
>> sense.
>>
>> Martin
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> --
>>
>> *It'll all be OK in the end. If it's not OK, it's not the end*
>>
>>
>>
>>
>>
>>
>> --
>> --
>> Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
>> <http://www.carolweaver.co.uk/Travel>
>> Plusnet -cardun if you sign up recommend me please
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>
>
> --
>
> *It'll all be OK in the end. If it's not OK, it's not the end*
>
>
>



--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
Plusnet -cardun if you sign up recommend me please

Jobsworth

Bennett Family
 

We turned up at the the CMC St David’s site on the day the Fastnet Race had been cancelled because of the gale and parts of Wales had been declared a disaster area.

Unsurprisingly, the site wasn’t crowded! We parked facing into the wind to avoid the battering and the Warden asked us to move as we were not in line with their marker post!

I refused and he said that if the fire brigade came to check I’d be in trouble. I did point out that
A. It’s a disaster area and surely the fire service had better things to do and
B. There was nobody else daft enough to be on the site!

Martin

On 16 Feb 2020, at 09:27, timsinc Sinclair via Groups.Io <timsinc=gmail.com@groups.io> wrote:

Thank you, Mr Jobsworth, for making camping such empowering, relaxed
fun......Definitely hooked up on it !!!.

Talking to a former CMC warden holidaying at this near Granada
campsite, relating some of the rules, such as tools (like even small
pair of plyers) on site had all to be of certain approved standard. As
did the box.

One day, a motorhomer asked him if he could borrow step ladder to sort
out a problem with high-up awning. "Sorry, we're not allowed to lend
any equipment". If he fell off, the club might be sued.

But what my ex-warden then said to the man: "I'm off to clean the loos
and the step ladder happens to be beside that gate over there."

Thankfully, they're not all Jobsworths. To be certain to avoid one,
give Henley-on-Thames CMC site a miss, although does depend on who is
on duty.

Campervan Tim

On 16/02/2020, Bennett Family <martin@...> wrote:
CMC rules seem to make cables of less than 23m “illegal” even if next to the
bollard - so best dump your short cable and ensure that your full sized
replacement has been supplied by the “caravan manufacturer” - would be as
well to have a receipt. Disconnect in very cold weather as it may not pass
the “flexible” test.

Jobsworth
On 16 Feb 2020, at 08:25, timsinc Sinclair via Groups.Io
<timsinc=gmail.com@groups.io> wrote:


Well, the CMC rules say: "The maximum permitted distance between socket
outlet and any point on the caravan pitch is 20 metres.
"The hook up lead should be 25 metres (+/- 2 metres) of flexible cable
supplied by the caravan manufacturer."
That's where and why, I suppose, joing together of two cables frowned upon.
The CCC have a much more relaxed attitude.

No mention of colour or size. Usual stuff about completely unwinding and not
leaving plugged into bollard if off for the day - or even doing the
empty/filling biz.

"Club site staff have authority to refuse to offer a power supply to a
caravan if it is believed that the installation may be unsafe."

Yep, often down to how officious a warden is.

Campervan Tim




On 15 February 2020 5:26:56 pm "Adrian Harman" <adrianharman@...>
wrote:

I’m also confused??

Adrian
On 15 Feb 2020, 17:24 +0000, Richard <edelec@...>, wrote:
I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard

On 15/02/2020 16:53, Carol Weaver wrote:

Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.

Carol

On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:

Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly
available on the market are orange 2.5mm. These meet the standards
of the NCC and the CCC.

Also available but not so common are orange 1.5mm but these are
not approved by the NCC.

I’ve hated using the two 2.5mm orange cables that I’ve owned
because they have quickly become inflexible, tangled and hard to
wind up.

So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
says on the pack that it’s not suitable for caravan sites and
should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.

Go Outdoors Price is £30 but I found it for £22 on another website
and with their price guarantee, they sold it to me for £20. Bargain!

I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian



On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
<mailto:timsinc@...>> wrote:

On 15/02/2020, Andy Clarke <andyclarke1050@...
<mailto:andyclarke1050@...>> wrote:
25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm


... and a heck of a lot easier to man/woman-handle. Except for CMC
sites, two even shorter cables connecting if needed (but rarely)
definitely my preferred option.

Campervan Tim
in storm-free, sunny Spain



UKMotorhomes.net

On Sat, 15 Feb 2020 at 12:33, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Andy, Ern

Thanks.

Any idea of the weight difference for a 25m length of each? I
doubt f it
will be significant in the grand scheme of things.

Martin


On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
<andyclarke1050=
gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:


1.5mm cable is OK for up to 3kW assuming an allowable voltage
drop of 5%
and that the cable is in free air, i.e. not on a reel or
closely coiled.

Andy Clarke
www.ukmotorhomes.net <http://www.ukmotorhomes.net>

On Fri, 14 Feb 2020 at 21:05, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Is there any advantage in using 2.5mm rather than 1.5mm given
that most
of us are unlikely to use more than 2kw?
Just demonstrating my ignorance.
If no advantage then the lighter weight, blue, cable would
seem to make
sense.

Martin










--

*It'll all be OK in the end. If it's not OK, it's not the end*






--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please











--

*It'll all be OK in the end. If it's not OK, it's not the end*


Re: EHU cable 1.5mm/2.5mm orange or blue?

timsinc Sinclair
 

Thank you, Mr Jobsworth, for making camping such empowering, relaxed
fun......Definitely hooked up on it !!!.

Talking to a former CMC warden holidaying at this near Granada
campsite, relating some of the rules, such as tools (like even small
pair of plyers) on site had all to be of certain approved standard. As
did the box.

One day, a motorhomer asked him if he could borrow step ladder to sort
out a problem with high-up awning. "Sorry, we're not allowed to lend
any equipment". If he fell off, the club might be sued.

But what my ex-warden then said to the man: "I'm off to clean the loos
and the step ladder happens to be beside that gate over there."

Thankfully, they're not all Jobsworths. To be certain to avoid one,
give Henley-on-Thames CMC site a miss, although does depend on who is
on duty.

Campervan Tim

On 16/02/2020, Bennett Family <martin@...> wrote:
CMC rules seem to make cables of less than 23m “illegal” even if next to the
bollard - so best dump your short cable and ensure that your full sized
replacement has been supplied by the “caravan manufacturer” - would be as
well to have a receipt. Disconnect in very cold weather as it may not pass
the “flexible” test.

Jobsworth
On 16 Feb 2020, at 08:25, timsinc Sinclair via Groups.Io
<timsinc=gmail.com@groups.io> wrote:


Well, the CMC rules say: "The maximum permitted distance between socket
outlet and any point on the caravan pitch is 20 metres.
"The hook up lead should be 25 metres (+/- 2 metres) of flexible cable
supplied by the caravan manufacturer."
That's where and why, I suppose, joing together of two cables frowned upon.
The CCC have a much more relaxed attitude.

No mention of colour or size. Usual stuff about completely unwinding and not
leaving plugged into bollard if off for the day - or even doing the
empty/filling biz.

"Club site staff have authority to refuse to offer a power supply to a
caravan if it is believed that the installation may be unsafe."

Yep, often down to how officious a warden is.

Campervan Tim




On 15 February 2020 5:26:56 pm "Adrian Harman" <adrianharman@...>
wrote:

I’m also confused??

Adrian
On 15 Feb 2020, 17:24 +0000, Richard <edelec@...>, wrote:
I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard

On 15/02/2020 16:53, Carol Weaver wrote:

Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.

Carol

On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:

Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly
available on the market are orange 2.5mm. These meet the standards
of the NCC and the CCC.

Also available but not so common are orange 1.5mm but these are
not approved by the NCC.

I’ve hated using the two 2.5mm orange cables that I’ve owned
because they have quickly become inflexible, tangled and hard to
wind up.

So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
says on the pack that it’s not suitable for caravan sites and
should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.

Go Outdoors Price is £30 but I found it for £22 on another website
and with their price guarantee, they sold it to me for £20. Bargain!

I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian



On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
<mailto:timsinc@...>> wrote:

On 15/02/2020, Andy Clarke <andyclarke1050@...
<mailto:andyclarke1050@...>> wrote:
25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm


... and a heck of a lot easier to man/woman-handle. Except for CMC
sites, two even shorter cables connecting if needed (but rarely)
definitely my preferred option.

Campervan Tim
in storm-free, sunny Spain



UKMotorhomes.net

On Sat, 15 Feb 2020 at 12:33, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Andy, Ern

Thanks.

Any idea of the weight difference for a 25m length of each? I
doubt f it
will be significant in the grand scheme of things.

Martin


On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
<andyclarke1050=
gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:


1.5mm cable is OK for up to 3kW assuming an allowable voltage
drop of 5%
and that the cable is in free air, i.e. not on a reel or
closely coiled.

Andy Clarke
www.ukmotorhomes.net <http://www.ukmotorhomes.net>

On Fri, 14 Feb 2020 at 21:05, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Is there any advantage in using 2.5mm rather than 1.5mm given
that most
of us are unlikely to use more than 2kw?
Just demonstrating my ignorance.
If no advantage then the lighter weight, blue, cable would
seem to make
sense.

Martin










--

*It'll all be OK in the end. If it's not OK, it's not the end*






--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please










--

*It'll all be OK in the end. If it's not OK, it's not the end*

Re: EHU cable 1.5mm/2.5mm orange or blue?

Sandytrax
 

This what I bought yesterday. Note it says not approved by NCC and not suitable for ‘caravan site use’. 
WTF!

https://www.maypole.ltd.uk/mp3772-230v-25m-extension-lead

Re: EHU cable 1.5mm/2.5mm orange or blue?

Carol Weaver
 


Didn’t know caravan manufacturers even made cables!!  No rule for Motorhome?


On Sun, 16 Feb 2020 at 08:41, Bennett Family <martin@...> wrote:
CMC rules seem to make cables of less than 23m “illegal” even if next to the bollard - so best dump your short cable and ensure that your full sized replacement has been supplied by the “caravan manufacturer” - would be as well to have a receipt. Disconnect in very cold weather as it may not pass the “flexible” test. 

Jobsworth 


On 16 Feb 2020, at 08:25, timsinc Sinclair via Groups.Io <timsinc=gmail.com@groups.io> wrote:


Well, the CMC rules say: "The maximum permitted distance between socket outlet and any point on the caravan pitch is 20 metres.
"The hook up lead should be 25 metres (+/- 2 metres) of flexible cable supplied by the caravan manufacturer."
That's where and why, I suppose, joing together of two cables frowned upon. The CCC have a much more relaxed attitude.

No mention of colour or size. Usual stuff about completely unwinding and not leaving plugged into bollard if off for the day - or even doing the empty/filling biz.

"Club site staff have authority to refuse to offer a power supply to a caravan if it is believed that the installation may be unsafe."

Yep, often down to how officious a warden is.

Campervan Tim



On 15 February 2020 5:26:56 pm "Adrian Harman" <adrianharman@...> wrote:

I’m also confused??

Adrian 
On 15 Feb 2020, 17:24 +0000, Richard <edelec@...>, wrote:
I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard

On 15/02/2020 16:53, Carol Weaver wrote:

Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.

Carol

On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:

Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly
available on the market are orange 2.5mm. These meet the standards
of the NCC and the CCC.

Also available but not so common are orange 1.5mm but these are
not approved by the NCC.

I’ve hated using the two 2.5mm orange cables that I’ve owned
because they have quickly become inflexible, tangled  and hard to
wind up.

So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
says on the pack that it’s not suitable for caravan sites and
should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.

Go Outdoors Price is £30 but I found it for £22 on another website
and with their price guarantee, they sold it to me for £20. Bargain!

I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian



On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
<mailto:timsinc@...>> wrote:

On 15/02/2020, Andy Clarke <andyclarke1050@...
<mailto:andyclarke1050@...>> wrote:
25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm


... and a heck of a lot easier to man/woman-handle. Except for CMC
sites, two even shorter cables connecting if needed (but rarely)
definitely my preferred option.

Campervan Tim
in storm-free, sunny Spain



UKMotorhomes.net

On Sat, 15 Feb 2020 at 12:33, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Andy, Ern

Thanks.

Any idea of the weight difference for a 25m length of each? I
doubt f it
will be significant in the grand scheme of things.

Martin


On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
<andyclarke1050=
gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:


1.5mm cable is OK for up to 3kW assuming an allowable voltage
drop of 5%
and that the cable is in free air, i.e. not on a reel or
closely coiled.

Andy Clarke
www.ukmotorhomes.net <http://www.ukmotorhomes.net>

On Fri, 14 Feb 2020 at 21:05, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Is there any advantage in using 2.5mm rather than 1.5mm given
that most
of us are unlikely to use more than 2kw?
Just demonstrating my ignorance.
If no advantage then the lighter weight, blue, cable would
seem to make
sense.

Martin










--

*It'll all be OK in the end. If it's not OK, it's not the end*






--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please






--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
Plusnet -cardun if you sign up recommend me please

Re: EHU cable 1.5mm/2.5mm orange or blue?

Bennett Family
 

CMC rules seem to make cables of less than 23m “illegal” even if next to the bollard - so best dump your short cable and ensure that your full sized replacement has been supplied by the “caravan manufacturer” - would be as well to have a receipt. Disconnect in very cold weather as it may not pass the “flexible” test. 

Jobsworth 


On 16 Feb 2020, at 08:25, timsinc Sinclair via Groups.Io <timsinc@...> wrote:


Well, the CMC rules say: "The maximum permitted distance between socket outlet and any point on the caravan pitch is 20 metres.
"The hook up lead should be 25 metres (+/- 2 metres) of flexible cable supplied by the caravan manufacturer."
That's where and why, I suppose, joing together of two cables frowned upon. The CCC have a much more relaxed attitude.

No mention of colour or size. Usual stuff about completely unwinding and not leaving plugged into bollard if off for the day - or even doing the empty/filling biz.

"Club site staff have authority to refuse to offer a power supply to a caravan if it is believed that the installation may be unsafe."

Yep, often down to how officious a warden is.

Campervan Tim



On 15 February 2020 5:26:56 pm "Adrian Harman" <adrianharman@...> wrote:

I’m also confused??

Adrian 
On 15 Feb 2020, 17:24 +0000, Richard <edelec@...>, wrote:
I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard

On 15/02/2020 16:53, Carol Weaver wrote:

Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.

Carol

On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:

Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly
available on the market are orange 2.5mm. These meet the standards
of the NCC and the CCC.

Also available but not so common are orange 1.5mm but these are
not approved by the NCC.

I’ve hated using the two 2.5mm orange cables that I’ve owned
because they have quickly become inflexible, tangled  and hard to
wind up.

So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
says on the pack that it’s not suitable for caravan sites and
should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.

Go Outdoors Price is £30 but I found it for £22 on another website
and with their price guarantee, they sold it to me for £20. Bargain!

I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian



On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
<mailto:timsinc@...>> wrote:

On 15/02/2020, Andy Clarke <andyclarke1050@...
<mailto:andyclarke1050@...>> wrote:
25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm


... and a heck of a lot easier to man/woman-handle. Except for CMC
sites, two even shorter cables connecting if needed (but rarely)
definitely my preferred option.

Campervan Tim
in storm-free, sunny Spain



UKMotorhomes.net

On Sat, 15 Feb 2020 at 12:33, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Andy, Ern

Thanks.

Any idea of the weight difference for a 25m length of each? I
doubt f it
will be significant in the grand scheme of things.

Martin


On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
<andyclarke1050=
gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:


1.5mm cable is OK for up to 3kW assuming an allowable voltage
drop of 5%
and that the cable is in free air, i.e. not on a reel or
closely coiled.

Andy Clarke
www.ukmotorhomes.net <http://www.ukmotorhomes.net>

On Fri, 14 Feb 2020 at 21:05, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Is there any advantage in using 2.5mm rather than 1.5mm given
that most
of us are unlikely to use more than 2kw?
Just demonstrating my ignorance.
If no advantage then the lighter weight, blue, cable would
seem to make
sense.

Martin










--

*It'll all be OK in the end. If it's not OK, it's not the end*






--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please






Re: EHU cable 1.5mm/2.5mm orange or blue?

timsinc Sinclair
 

Well, the CMC rules say: "The maximum permitted distance between socket outlet and any point on the caravan pitch is 20 metres.
"The hook up lead should be 25 metres (+/- 2 metres) of flexible cable supplied by the caravan manufacturer."
That's where and why, I suppose, joing together of two cables frowned upon. The CCC have a much more relaxed attitude.

No mention of colour or size. Usual stuff about completely unwinding and not leaving plugged into bollard if off for the day - or even doing the empty/filling biz.

"Club site staff have authority to refuse to offer a power supply to a caravan if it is believed that the installation may be unsafe."

Yep, often down to how officious a warden is.

Campervan Tim



On 15 February 2020 5:26:56 pm "Adrian Harman" <adrianharman@...> wrote:

I’m also confused??

Adrian 
On 15 Feb 2020, 17:24 +0000, Richard <edelec@...>, wrote:
I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard

On 15/02/2020 16:53, Carol Weaver wrote:

Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.

Carol

On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:

Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly
available on the market are orange 2.5mm. These meet the standards
of the NCC and the CCC.

Also available but not so common are orange 1.5mm but these are
not approved by the NCC.

I’ve hated using the two 2.5mm orange cables that I’ve owned
because they have quickly become inflexible, tangled  and hard to
wind up.

So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
says on the pack that it’s not suitable for caravan sites and
should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.

Go Outdoors Price is £30 but I found it for £22 on another website
and with their price guarantee, they sold it to me for £20. Bargain!

I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian



On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
<mailto:timsinc@...>> wrote:

On 15/02/2020, Andy Clarke <andyclarke1050@...
<mailto:andyclarke1050@...>> wrote:
25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm


... and a heck of a lot easier to man/woman-handle. Except for CMC
sites, two even shorter cables connecting if needed (but rarely)
definitely my preferred option.

Campervan Tim
in storm-free, sunny Spain



UKMotorhomes.net

On Sat, 15 Feb 2020 at 12:33, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Andy, Ern

Thanks.

Any idea of the weight difference for a 25m length of each? I
doubt f it
will be significant in the grand scheme of things.

Martin


On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
<andyclarke1050=
gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:


1.5mm cable is OK for up to 3kW assuming an allowable voltage
drop of 5%
and that the cable is in free air, i.e. not on a reel or
closely coiled.

Andy Clarke
www.ukmotorhomes.net <http://www.ukmotorhomes.net>

On Fri, 14 Feb 2020 at 21:05, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Is there any advantage in using 2.5mm rather than 1.5mm given
that most
of us are unlikely to use more than 2kw?
Just demonstrating my ignorance.
If no advantage then the lighter weight, blue, cable would
seem to make
sense.

Martin










--

*It'll all be OK in the end. If it's not OK, it's not the end*






--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please






Re: EHU cable 1.5mm/2.5mm orange or blue?

Adrian Harman
 

I’m also confused??

Adrian 

On 15 Feb 2020, 17:24 +0000, Richard <edelec@...>, wrote:
I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard

On 15/02/2020 16:53, Carol Weaver wrote:

Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.

Carol

On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:

Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly
available on the market are orange 2.5mm. These meet the standards
of the NCC and the CCC.

Also available but not so common are orange 1.5mm but these are
not approved by the NCC.

I’ve hated using the two 2.5mm orange cables that I’ve owned
because they have quickly become inflexible, tangled  and hard to
wind up.

So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
says on the pack that it’s not suitable for caravan sites and
should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.

Go Outdoors Price is £30 but I found it for £22 on another website
and with their price guarantee, they sold it to me for £20. Bargain!

I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian



On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
<mailto:timsinc@...>> wrote:

On 15/02/2020, Andy Clarke <andyclarke1050@...
<mailto:andyclarke1050@...>> wrote:
25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm


... and a heck of a lot easier to man/woman-handle. Except for CMC
sites, two even shorter cables connecting if needed (but rarely)
definitely my preferred option.

Campervan Tim
in storm-free, sunny Spain



UKMotorhomes.net

On Sat, 15 Feb 2020 at 12:33, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Andy, Ern

Thanks.

Any idea of the weight difference for a 25m length of each? I
doubt f it
will be significant in the grand scheme of things.

Martin


On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
<andyclarke1050=
gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:


1.5mm cable is OK for up to 3kW assuming an allowable voltage
drop of 5%
and that the cable is in free air, i.e. not on a reel or
closely coiled.

Andy Clarke
www.ukmotorhomes.net <http://www.ukmotorhomes.net>

On Fri, 14 Feb 2020 at 21:05, Bennett Family
<martin@... <mailto:martin@...>>
wrote:

Is there any advantage in using 2.5mm rather than 1.5mm given
that most
of us are unlikely to use more than 2kw?
Just demonstrating my ignorance.
If no advantage then the lighter weight, blue, cable would
seem to make
sense.

Martin










--

*It'll all be OK in the end. If it's not OK, it's not the end*






--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please





Re: EHU cable 1.5mm/2.5mm orange or blue?

Richard
 

Apologies should read

I am amazed at what I am reading! What are these caravan site actual
rules with regard to cables?
Richard

On 15/02/2020 17:24, Edelec wrote:
I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard

On 15/02/2020 16:53, Carol Weaver wrote:

Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.

Carol

On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:

    Thanks to all for your thoughts.
    My further research indicates that standard ehu cables commonly
    available on the market are orange 2.5mm. These meet the standards
    of the NCC and the CCC.

    Also available but not so common are orange 1.5mm but these are
    not approved by the NCC.

    I’ve hated using the two 2.5mm orange cables that I’ve owned
    because they have quickly become inflexible, tangled  and hard to
    wind up.

    So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
    says on the pack that it’s not suitable for caravan sites and
    should not be used in wet or damp conditions!!
    However, it is marketed as a Motorhome ehu on many websites.
    So that’s a bit mysterious.

    Go Outdoors Price is £30 but I found it for £22 on another website
    and with their price guarantee, they sold it to me for £20. Bargain!

    I’m sure it will be fine.
    And my heart won’t sink when I need to use a hook up.
    Cheers
    Brian



    > On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
    <mailto:timsinc@...>> wrote:
    >
    > On 15/02/2020, Andy Clarke <andyclarke1050@...
    <mailto:andyclarke1050@...>> wrote:
    >> 25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
    >>
    >
    > ... and a heck of a lot easier to man/woman-handle. Except for CMC
    > sites, two even shorter cables connecting if needed (but rarely)
    > definitely my preferred option.
    >
    > Campervan Tim
    > in storm-free, sunny Spain
    >
    >
    >
    >> UKMotorhomes.net
    >>
    >>> On Sat, 15 Feb 2020 at 12:33, Bennett Family
    <martin@... <mailto:martin@...>>
    >>> wrote:
    >>>
    >>> Andy, Ern
    >>>
    >>> Thanks.
    >>>
    >>> Any idea of the weight difference for a 25m length of each? I
    doubt f it
    >>> will be significant in the grand scheme of things.
    >>>
    >>> Martin
    >>>
    >>>
    >>> On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
    <andyclarke1050=
    >>> gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:
    >>>
    >>> 
    >>> 1.5mm cable is OK for up to 3kW assuming an allowable voltage
    drop of 5%
    >>> and that the cable is in free air, i.e. not on a reel or
    closely coiled.
    >>>
    >>> Andy Clarke
    >>> www.ukmotorhomes.net <http://www.ukmotorhomes.net>
    >>>
    >>> On Fri, 14 Feb 2020 at 21:05, Bennett Family
    <martin@... <mailto:martin@...>>
    >>> wrote:
    >>>
    >>>> Is there any advantage in using 2.5mm rather than 1.5mm given
    that most
    >>>> of us are unlikely to use more than 2kw?
    >>>> Just demonstrating my ignorance.
    >>>> If no advantage then the lighter weight, blue, cable would
    seem to make
    >>>> sense.
    >>>>
    >>>> Martin
    >>>>
    >>>>
    >>>
    >>>
    >>
    >>
    >>
    >>
    >
    >
    > --
    >
    > *It'll all be OK in the end. If it's not OK, it's not the end*
    >
    >
    >



--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please

Re: EHU cable 1.5mm/2.5mm orange or blue?

Richard
 

I am amazed at what I am reading! What are these caravan rules with
regard to cables?
Richard

On 15/02/2020 16:53, Carol Weaver wrote:

Well our blue one has been used on both CCC and old CC (not in latter
now) without any problems.

Carol

On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...
<mailto:brianinspain12@...>> wrote:

Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly
available on the market are orange 2.5mm. These meet the standards
of the NCC and the CCC.

Also available but not so common are orange 1.5mm but these are
not approved by the NCC.

I’ve hated using the two 2.5mm orange cables that I’ve owned
because they have quickly become inflexible, tangled  and hard to
wind up.

So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It
says on the pack that it’s not suitable for caravan sites and
should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.

Go Outdoors Price is £30 but I found it for £22 on another website
and with their price guarantee, they sold it to me for £20. Bargain!

I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian



> On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...
<mailto:timsinc@...>> wrote:
>
> On 15/02/2020, Andy Clarke <andyclarke1050@...
<mailto:andyclarke1050@...>> wrote:
>> 25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
>>
>
> ... and a heck of a lot easier to man/woman-handle. Except for CMC
> sites, two even shorter cables connecting if needed (but rarely)
> definitely my preferred option.
>
> Campervan Tim
> in storm-free, sunny Spain
>
>
>
>> UKMotorhomes.net
>>
>>> On Sat, 15 Feb 2020 at 12:33, Bennett Family
<martin@... <mailto:martin@...>>
>>> wrote:
>>>
>>> Andy, Ern
>>>
>>> Thanks.
>>>
>>> Any idea of the weight difference for a 25m length of each? I
doubt f it
>>> will be significant in the grand scheme of things.
>>>
>>> Martin
>>>
>>>
>>> On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io
<andyclarke1050=
>>> gmail.com@groups.io <mailto:gmail.com@groups.io>> wrote:
>>>
>>> 
>>> 1.5mm cable is OK for up to 3kW assuming an allowable voltage
drop of 5%
>>> and that the cable is in free air, i.e. not on a reel or
closely coiled.
>>>
>>> Andy Clarke
>>> www.ukmotorhomes.net <http://www.ukmotorhomes.net>
>>>
>>> On Fri, 14 Feb 2020 at 21:05, Bennett Family
<martin@... <mailto:martin@...>>
>>> wrote:
>>>
>>>> Is there any advantage in using 2.5mm rather than 1.5mm given
that most
>>>> of us are unlikely to use more than 2kw?
>>>> Just demonstrating my ignorance.
>>>> If no advantage then the lighter weight, blue, cable would
seem to make
>>>> sense.
>>>>
>>>> Martin
>>>>
>>>>
>>>
>>>
>>
>>
>>
>>
>
>
> --
>
> *It'll all be OK in the end. If it's not OK, it's not the end*
>
>
>



--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
<http://www.carolweaver.co.uk/Travel>
Plusnet -cardun if you sign up recommend me please

Re: EHU cable 1.5mm/2.5mm orange or blue?

Carol Weaver
 


Well our blue one has been used on both CCC and old CC (not in latter now) without any problems. 

Carol


On Sat, 15 Feb 2020 at 16:49, Sandytrax <brianinspain12@...> wrote:
Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly available on the market are orange 2.5mm. These meet the standards of the NCC and the CCC.

Also available but not so common are orange 1.5mm but these are not approved by the NCC.

I’ve hated using the two 2.5mm orange cables that I’ve owned because they have quickly become inflexible, tangled  and hard to wind up.

So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It says on the pack that it’s not suitable for caravan sites and should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.

Go Outdoors Price is £30 but I found it for £22 on another website and with their price guarantee, they sold it to me for £20. Bargain!

I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian



> On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...> wrote:
>
> On 15/02/2020, Andy Clarke <andyclarke1050@...> wrote:
>> 25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
>>
>
> ... and a heck of a lot easier to man/woman-handle. Except for CMC
> sites, two even shorter cables connecting if needed (but rarely)
> definitely my preferred option.
>
> Campervan Tim
> in storm-free, sunny Spain
>
>
>
>> UKMotorhomes.net
>>
>>> On Sat, 15 Feb 2020 at 12:33, Bennett Family <martin@...>
>>> wrote:
>>>
>>> Andy, Ern
>>>
>>> Thanks.
>>>
>>> Any idea of the weight difference for a 25m length of each? I doubt f it
>>> will be significant in the grand scheme of things.
>>>
>>> Martin
>>>
>>>
>>> On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io <andyclarke1050=
>>> gmail.com@groups.io> wrote:
>>>
>>> 
>>> 1.5mm cable is OK for up to 3kW assuming an allowable voltage drop of 5%
>>> and that the cable is in free air, i.e. not on a reel or closely coiled.
>>>
>>> Andy Clarke
>>> www.ukmotorhomes.net
>>>
>>> On Fri, 14 Feb 2020 at 21:05, Bennett Family <martin@...>
>>> wrote:
>>>
>>>> Is there any advantage in using 2.5mm rather than 1.5mm given that most
>>>> of us are unlikely to use more than 2kw?
>>>> Just demonstrating my ignorance.
>>>> If no advantage then the lighter weight, blue, cable would seem to make
>>>> sense.
>>>>
>>>> Martin
>>>>
>>>>
>>>
>>>
>>
>>
>>
>>
>
>
> --
>
> *It'll all be OK in the end. If it's not OK, it's not the end*
>
>
>



--
--
Carol WeaverAires photos here|. www.carolweaver.co.uk/Travel
Plusnet -cardun if you sign up recommend me please

Re: EHU cable 1.5mm/2.5mm orange or blue?

Sandytrax
 

Thanks to all for your thoughts.
My further research indicates that standard ehu cables commonly available on the market are orange 2.5mm. These meet the standards of the NCC and the CCC.

Also available but not so common are orange 1.5mm but these are not approved by the NCC.

I’ve hated using the two 2.5mm orange cables that I’ve owned because they have quickly become inflexible, tangled and hard to wind up.

So I’ve just bought a 25m orange 1.5 cable from Go Outdoors. It says on the pack that it’s not suitable for caravan sites and should not be used in wet or damp conditions!!
However, it is marketed as a Motorhome ehu on many websites.
So that’s a bit mysterious.

Go Outdoors Price is £30 but I found it for £22 on another website and with their price guarantee, they sold it to me for £20. Bargain!

I’m sure it will be fine.
And my heart won’t sink when I need to use a hook up.
Cheers
Brian

On 15 Feb 2020, at 13:17, timsinc Sinclair <timsinc@...> wrote:

On 15/02/2020, Andy Clarke <andyclarke1050@...> wrote:
25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
... and a heck of a lot easier to man/woman-handle. Except for CMC
sites, two even shorter cables connecting if needed (but rarely)
definitely my preferred option.

Campervan Tim
in storm-free, sunny Spain



UKMotorhomes.net

On Sat, 15 Feb 2020 at 12:33, Bennett Family <martin@...>
wrote:

Andy, Ern

Thanks.

Any idea of the weight difference for a 25m length of each? I doubt f it
will be significant in the grand scheme of things.

Martin


On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io <andyclarke1050=
gmail.com@groups.io> wrote:


1.5mm cable is OK for up to 3kW assuming an allowable voltage drop of 5%
and that the cable is in free air, i.e. not on a reel or closely coiled.

Andy Clarke
www.ukmotorhomes.net

On Fri, 14 Feb 2020 at 21:05, Bennett Family <martin@...>
wrote:

Is there any advantage in using 2.5mm rather than 1.5mm given that most
of us are unlikely to use more than 2kw?
Just demonstrating my ignorance.
If no advantage then the lighter weight, blue, cable would seem to make
sense.

Martin




--

*It'll all be OK in the end. If it's not OK, it's not the end*


Re: EHU cable 1.5mm/2.5mm orange or blue?

timsinc Sinclair
 

On 15/02/2020, Andy Clarke <andyclarke1050@...> wrote:
25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm
... and a heck of a lot easier to man/woman-handle. Except for CMC
sites, two even shorter cables connecting if needed (but rarely)
definitely my preferred option.

Campervan Tim
in storm-free, sunny Spain



UKMotorhomes.net

On Sat, 15 Feb 2020 at 12:33, Bennett Family <martin@...>
wrote:

Andy, Ern

Thanks.

Any idea of the weight difference for a 25m length of each? I doubt f it
will be significant in the grand scheme of things.

Martin


On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io <andyclarke1050=
gmail.com@groups.io> wrote:


1.5mm cable is OK for up to 3kW assuming an allowable voltage drop of 5%
and that the cable is in free air, i.e. not on a reel or closely coiled.

Andy Clarke
www.ukmotorhomes.net

On Fri, 14 Feb 2020 at 21:05, Bennett Family <martin@...>
wrote:

Is there any advantage in using 2.5mm rather than 1.5mm given that most
of us are unlikely to use more than 2kw?
Just demonstrating my ignorance.
If no advantage then the lighter weight, blue, cable would seem to make
sense.

Martin




--

*It'll all be OK in the end. If it's not OK, it's not the end*

Re: EHU cable 1.5mm/2.5mm orange or blue?

Bennett Family
 

Thanks - every little helps when limited to 3,500kg, but I think I should start by shedding quite a few kilos myself!

Martin


On 15 Feb 2020, at 12:58, Andy Clarke via Groups.Io <andyclarke1050@...> wrote:


25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm

Andy Clarke
UKMotorhomes.net

On Sat, 15 Feb 2020 at 12:33, Bennett Family <martin@...> wrote:
Andy, Ern

Thanks.

Any idea of the weight difference for a 25m length of each? I doubt f it will be significant in the grand scheme of things.

Martin


On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io <andyclarke1050=gmail.com@groups.io> wrote:


1.5mm cable is OK for up to 3kW assuming an allowable voltage drop of 5% and that the cable is in free air, i.e. not on a reel or closely coiled.

Andy Clarke

On Fri, 14 Feb 2020 at 21:05, Bennett Family <martin@...> wrote:
Is there any advantage in using 2.5mm rather than 1.5mm given that most of us are unlikely to use more than 2kw?
Just demonstrating my ignorance. 
If no advantage then the lighter weight, blue, cable would seem to make sense. 

Martin

Re: EHU cable 1.5mm/2.5mm orange or blue?

Andy Clarke
 

25m of 1.5mm is approx 1.5kg lighter that 25m of 2.5mm

Andy Clarke
UKMotorhomes.net

On Sat, 15 Feb 2020 at 12:33, Bennett Family <martin@...> wrote:
Andy, Ern

Thanks.

Any idea of the weight difference for a 25m length of each? I doubt f it will be significant in the grand scheme of things.

Martin


On 15 Feb 2020, at 12:21, Andy Clarke via Groups.Io <andyclarke1050=gmail.com@groups.io> wrote:


1.5mm cable is OK for up to 3kW assuming an allowable voltage drop of 5% and that the cable is in free air, i.e. not on a reel or closely coiled.

Andy Clarke

On Fri, 14 Feb 2020 at 21:05, Bennett Family <martin@...> wrote:
Is there any advantage in using 2.5mm rather than 1.5mm given that most of us are unlikely to use more than 2kw?
Just demonstrating my ignorance. 
If no advantage then the lighter weight, blue, cable would seem to make sense. 

Martin